SCOPE
An existing electric range is being changed out to a gas range.
PROBLEM
The existing recept for the electric range is a 50A, 125/250V, 4W. The new range is gas and a 20A ,120V, 3W recept is needed.
PROPOSED SOLUTION
I may be incorrect with my solution and this is where I'm asking for help.
Here is what I thought of doing...
QUESTIONS
1. Is there anything in the 13-step proposed solution above that I got wrong or that I've missed?
2. In the breaker panel, step #10 above, according to NEC 312.8 (A), wire-nut inside of the breaker panel is permitted, do I have that correct?
Pictures can be viewed here----->Range Recept.
PROBLEM
PROPOSED SOLUTION
BEHIND RANGE
1. Cut out the drywall and install a new box to the left of the existing recept box.
2. Remove the existing 4W recept and utilize the box as a junction point.
3. Cap the B-phase wire in the existing box.
4. Wire-nut A-phase hot, neutral, and ground with 12-3 romex in existing box.
5. Bring 12-3 romex into the new box.
6. Install 20A, 120V, 3W recept into new box.
7. Blank plate the existing recept box.
BREAKER PANEL
8. Remove the existing 50A, 2P breaker in panel.
9. Cap the B-phase wire in breaker panel and label it.
10. Wire-nut 12ga black onto existing #6 A-phase wire.
11. Install a new 20A, 1P arc-fault breaker on A-phase in panel.
12. Install a filler plate on B-phase of cb panel cover.
13. Re-label panel schedule accordingly.
QUESTIONS