When talking voltage configuration, the equipment grounding conductor (EGC) is NOT in the count. The "W" number is the number of circuit conductors. Though required, the EGC is not a circuit conductor. 208/120V 3Ø 4W is a voltage configuration which includes the neutral, i.e. four circuit conductors.Yes. 3 poles 4 wires where the 4th wire is earth ground not neutral. 3P + PE
What you want doesn't even have 120V, so it'd be 208V 3Ø 3W.
That is different from the number of wires designated on a cord, which includes the conductor with green insulation. 6/4 SOOW has four wires and in that count, one has green insulation.
Don't blame me for the disparity. I did not set the conventions. I'm just the messenger.
PS: I should note that when dealing with cable (not cord) with a designated EGC, the EGC is not counted in the cable conductor designation. For example 12/3 MC has a black, a red, a white, and a green wire.