6 disconnect rule violation?

Status
Not open for further replies.

jbwhite

Senior Member
Re: 6 disconnect rule violation?

jwelectric, we are having chili too... :)

happy holidays. and does this thead approach the top for most posts yet, or do we need to throw another wrench in?
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: 6 disconnect rule violation?

Mike Merry Christmas enjoy the Chili, my turkey is getting close to done. :)

For extra points can I supply a straight 240 appliance like a water heater with single pole breakers?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: 6 disconnect rule violation?

Did someone say Chili? ;)

Turkey tomorrow, snacking tonight.

Merry Christmas guys.


Roger
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
Re: 6 disconnect rule violation?

Originally posted by jwelectric:
Take a look at 210.7 and you will see that what we were talking about is two separate circuits landing on the SAME device that is on ONE yoke. His statement was that the tabs could be broke off both the phase and neutral with two neutrals and two hots from the same phase in the panel landing on this single device. Wrong answer.
So, is there crow coming on this aspect of it too, Mike? :D

mwbcvsmbcs.jpg
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
Re: 6 disconnect rule violation?

Originally posted by iwire:
For extra points can I supply a straight 240 appliance like a water heater with single pole breakers?
I would say "no", 240.20(B) requires the breaker to open all conductors of the circuit. But I get the impression there's a trap here I just meandered into.

But I don't mind. :D
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: 6 disconnect rule violation?

Originally posted by georgestolz:
Originally posted by iwire:
For extra points can I supply a straight 240 appliance like a water heater with single pole breakers?
I would say "no", 240.20(B) requires the breaker to open all conductors of the circuit.
Yes that is true until you get to 240.20(B)(2).

In some cases two single pole breakers with handle ties can supply a line line load.

240.20(B)(2) Grounded Single-Phase and 3-wire dc Circuits. In grounded systems, individual single-pole circuit breakers with approved handle ties shall be permitted as the protection for each ungrounded conductor for line-to-line connected loads for single-phase circuits or 3-wire, direct-current circuits.
Originally posted by georgestolz:
But I get the impression there's a trap here I just meandered into.
Now why would you think that of me? :D
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
Re: 6 disconnect rule violation?

I even read that! :D

edit edit: Let's see if I edited out my brainfart fast enough noone saw it.

[ December 25, 2005, 10:11 AM: Message edited by: georgestolz ]
 