Pulled conductors in thru pvc pipe underground, from the main panel to a sub panel. Pulled in a # 6 cu for the ground and taped it green. Was surprised when the inspector said the # 6 ground wire has to be green and could not be identified using green tape.
Took me awhile to find it but section 250.119 (A) does cover it. Has to be larger than # 6 to be able to identify the ground wire using green tape.
What a surprise! I use # 10 green wire but always taped the black # 8 and/ or # 6 with green tape to identify it as a ground wire.
What's the reason or logic for having to use green wire as the ground, when using wire smaller than # 4. The code allows you to use tape to identify the phase legs when using #8 or #6 wire but you can't use tape on the same size ground wire! I appreciate your thoughts and ideas.
Took me awhile to find it but section 250.119 (A) does cover it. Has to be larger than # 6 to be able to identify the ground wire using green tape.
What a surprise! I use # 10 green wire but always taped the black # 8 and/ or # 6 with green tape to identify it as a ground wire.
What's the reason or logic for having to use green wire as the ground, when using wire smaller than # 4. The code allows you to use tape to identify the phase legs when using #8 or #6 wire but you can't use tape on the same size ground wire! I appreciate your thoughts and ideas.