Cavie
Senior Member
- Location
- SW Florida
The same requirement holds for the neutral also. No tape 6 and under
Easy Money said:Pulled conductors in thru pvc pipe underground, from the main panel to a sub panel. Pulled in a # 6 cu for the ground and taped it green. Was surprised when the inspector said the # 6 ground wire has to be green and could not be identified using green tape.
Took me awhile to find it but section 250.119 (A) does cover it. Has to be larger than # 6 to be able to identify the ground wire using green tape.
What a surprise! I use # 10 green wire but always taped the black # 8 and/ or # 6 with green tape to identify it as a ground wire.
What's the reason or logic for having to use green wire as the ground, when using wire smaller than # 4. The code allows you to use tape to identify the phase legs when using #8 or #6 wire but you can't use tape on the same size ground wire! I appreciate your thoughts and ideas.
jrannis said:The #6 roll goes quicker because I use it for connecting to ground rods.
Roger, although it does'nt say anything about color, it is allowed to be insulated.roger said:Not by code.
Roger
I agree Rick, I have to retract my earlier post but I will add, that if we use an insulated conductor it can be any color except white or gray. :smile:RUWired said:Roger, although it does'nt say anything about color, it is allowed to be insulated.
250.62 Grounding Electrode Conductor Material
The grounding electrode conductor shall be of copper, aluminum, or copper-clad aluminum. The material selected shall be resistant to any corrosive condition existing at the installation or shall be suitably protected against corrosion. The conductor shall be solid or stranded, insulated, covered, or bare.
480sparky said:Just use black. Tell the inspector it's green. Very, very dark dreen. :grin:
The NEC is concerned ONLY with safety
220/221 said:That's why they allow exposed cables and unfused service entrance conductors in a house.