krussell@scs-usa.com said:
I have 350amp overhead service feeding a 450 Amp meter can. I doube lugged the bottom of the meter can and came into the 2 seperate fused disconnects. (I came strieght out of the bottom of the can into a gutter and then up into each disconnect) I have one disconnect fused at 200 Amps feeding the house (A long way off) and a seperate disconect for feeding a seperated disconect fused at 125 Amps (for gate operator and shop to be added later). I have the meter grounded with # 6 Solid...I am taking the power underground to the house 400' away where there will be a breaker box and a seperate grounding rod....I think this clears up most of the questions yall had.
I didn't have any questions but I can say your GEC meets code and if its application is not going to get damaged it's extremely safe at #6.
Your utility service ends at the service disconnect not meter bases or meter equipment, in your case its the 200A & 125A disconnects, the service is usually not sized at OCP totals from service disconnect but
it is sized as per the calculated load in Article 220 (see Annex D Example D2, it's a simple one to use). The meter base/cans are not considered service equipment therefore its load circuitry remains service and not feeder, meaning its load will be easement - it is without short circuit/ground fault protection - to the service disconnect['s] so it must be treated with care and that is why if the service disconnect is installed inside the building it must be nearest the service point of entry.
The circuitry leaving your service disconnects are "feeders" and Article 225 applies if your feeding from a power pole structure, these circuits are not utility "services" and there is no easement required for them. These feeders will most likely be 4W (2 phases, 1 neutral, & 1 EGC) unless you meet
ALL the criteria of 250-32(B)(2) - which is eliminated in 2008. You need to size these feeders as per the calculated load from Article 220, and if you do account for voltage drop you'll need to adjust your EGC larger proportionally with the phase conductors and not just use Table 250-122 because it will be too small.
Your grounding electrodes at every building and structure - even power pole with service disconnects - must all interconnect and this will be done through the EGC. Again do not bond the neutral past the service disconnect unless you meet
ALL the criteria of 250-32(B)(2), see 250-24(5) & 250-142(B).
This is the fun stuff of our trade