fisherelectric
- Northern Va
Fisher-- if you hit the quote button on the bottom right of the post that you want to quote then it will be blocked like your quote is in my post.
Like that?
Like that?
am biding on a residence calling for 600 amp single phase metered panel feeding 3 200 amp panels the calculated load is 551 amps
Question anyone know of a link to this panel type also is the panel sufficient for this calculated load does the 80% rule apply here
Here lets stay with the 551 amps and a Calculator ....
551 / 3 =183.67
183.67/200MB=0.91835
VS
183.67/225MB=0.8163
183.67/250MB=0.734
Seems you short on Panel and Wire...
It's a house. Put a little heat and a little a/c in each one, and you're probably going to be good to go. I'd probably go for more than 3 panels though, too, but in another way. Each of those 200 amp panels would likely have a distributed subpanel someplace in the house hung off it for lighting and receptacles.
A house with a 600 amp service might have a pretty decent set of plans already with panel schedules and so on.