A ct is a current transformer cabinet for the CT's that the poco installs on large services.whats a CT,MLO,MB panel.I 'm trying to figure out what you guys are talking about.Thank you gentlemen.
whats a CT,MLO,MB panel.I 'm trying to figure out what you guys are talking about.Thank you gentlemen.
How about CT cabinet ----->gutter----->3 -200 amp main breaker panels grouped in one location?
Why not:
CT cabinet (& meter panel)----->gutter----->2-200 MB & 1-250MB w/200 MB for their isolated (MLO) panel?
The 250 will be lightly loaded. ??
If the ampacity of 4/0 al is 180amps and you use the next higher breaker, why wouldn't a 200amp breaker be compliant for 4/0 al?
am biding on a residence calling for 600 amp single phase metered panel feeding 3 200 amp panels the calculated load is 551 amps
If the ampacity of 4/0 al is 180amps and you use the next higher breaker, why wouldn't a 200amp breaker be compliant for 4/0 al?
The load on the panel served by the 200amp disconnect and SER is what matters.
What other problems?
If we are talking about ser cable here and we are using the 08 code then 4/0 is only good for 150 amps
What if the three panels are located outside?
"If we are talking about ser cable here and we are using the 08 code then 4/0 is only good for 150 amps "
Ok, got it. They have really made it expensive to put in a 200a disco and remote panel now.
Yeah- that's likely huh....