am biding on a residence calling for 600 amp single phase metered panel feeding 3 200 amp panels the calculated load is 551 amps
Question anyone know of a link to this panel type also is the panel sufficient for this calculated load does the 80% rule apply here
Here lets stay with the 551 amps and a Calculator ....
551 / 3 =183.67
183.67/200MB=0.91835
VS
183.67/225MB=0.8163
183.67/250MB=0.734
Seems you short on Panel and Wire...
It's a house. Put a little heat and a little a/c in each one, and you're probably going to be good to go. I'd probably go for more than 3 panels though, too, but in another way. Each of those 200 amp panels would likely have a distributed subpanel someplace in the house hung off it for lighting and receptacles.
A house with a 600 amp service might have a pretty decent set of plans already with panel schedules and so on.