I have an existing equipment connecting cord-set labeled; "600V, 400A"
Can I use that set of cord to connect the new equipment operating @ 500A , 208V, 3 phase????

What is the max. draw from that cord if the system is 120/208V ?????

Thank you
 
Hi ,
I have an existing equipment connecting cord-set labeled; "600V, 400A"
Can I use that set of cord to connect the new equipment operating @ 500A , 208V, 3 phase????

What is the max. draw from that cord if the system is 120/208V ?????

Thank you
400A I would have said. Dropping the voltage doesn't generally increase the current rating of a conductor.
 
In addition, that 400 amp rating may be a manufacturer's rating and may not be compliant with the rules found in the NEC.
 
Hi ,
I have an existing equipment connecting cord-set labeled; "600V, 400A"
Can I use that set of cord to connect the new equipment operating @ 500A , 208V, 3 phase????

What is the max. draw from that cord if the system is 120/208V ?????

Thank you

The answer is that you need to match the ampacity of the cordset to how much current the equipment draws. The voltage rating is about the insulation.

It seems unlikely you would have a piece of equipment that operates at exactly 500 A.

I have also never seen a cord set that is factory labeled as 400 A. The plugs might be labeled that way, but not the cord set.

Perhaps a picture of the label of the cord and the equipment nameplate would be in order.
 
The answer is that you need to match the ampacity of the cordset to how much current the equipment draws. The voltage rating is about the insulation.

It seems unlikely you would have a piece of equipment that operates at exactly 500 A.

I have also never seen a cord set that is factory labeled as 400 A. The plugs might be labeled that way, but not the cord set.

Perhaps a picture of the label of the cord and the equipment nameplate would be in order.

that label is on head /plug of the cord:thumbsup::thumbsup::thumbsup:
 
that label is on head /plug of the cord:thumbsup::thumbsup::thumbsup:
So that means the connector is rated 400 amps. Is possible only 325 amacity is needed, but 400 amp plug is next standard size, only 325 amp conductor would still be sufficient in many cases.
 
The answer is that you need to match the ampacity of the cordset to how much current the equipment draws. The voltage rating is about the insulation.

It seems unlikely you would have a piece of equipment that operates at exactly 500 A.
But would you chance it? Even if NEC allowed it?
I think the question has been answered with a simple "no".
The very fact that the question was asked suggests that a more complex answer would be superfluous.
The KISS principle comes to mind.
 
But would you chance it? Even if NEC allowed it?
I think the question has been answered with a simple "no".
The very fact that the question was asked suggests that a more complex answer would be superfluous.
The KISS principle comes to mind.

I don't think we know enough about the particulars to make any firm judgement. But in general I agree that if something is stated to be a 500 A load it would be a bad idea to use cords that are only good for 400 A.

incidentally, it is pretty common for people using Camlok style plugs to use conductor ampacities that far exceed what the NEC would allow. It is not clear to me that this is especially unsafe given how prevalent it is.
 
I don't think we know enough about the particulars to make any firm judgement.
We know that the cord-set is rated at 400A according to the OP.
Would you even remotely consider running it at 500A?

For me, and others it would seem, the answer is a simple one word response. That's the sum and substance of it.

It's easy to overthink a point.
Kiss principle applies.
 
We know that the cord-set is rated at 400A according to the OP.
Would you even remotely consider running it at 500A?

For me, and others it would seem, the answer is a simple one word response. That's the sum and substance of it.

It's easy to overthink a point.
Kiss principle applies.

I don't know what the 500 A thing means. I never heard of a 500A plug and it would not be a standard ampacity of any cable I can remember seeing. Therefore it suggests it is just something someone made up, especially being an even number like that.

I am not suggesting running 500 A thru a cord set that is unsafe to run at that level of current. But I am not sure what the OP actually has given the peculiar ratings he is stating.
 
I don't know what the 500 A thing means. I never heard of a 500A plug and it would not be a standard ampacity of any cable I can remember seeing. Therefore it suggests it is just something someone made up, especially being an even number like that.
I could be made up. Or theoretical. The answer remains the same.
 
The only thing OP has confirmed is the cord connector is rated 400 amps. We don't know if the load is actually 500 amps or if it is 500 amp overcurrent protection - which could be to allow for motor starting though the full load is under 400.
 