zbang
Senior Member
- Location
- Roughly 5346 miles from Earls Court
incidentally, it is pretty common for people using Camlok style plugs to use conductor ampacities that far exceed what the NEC would allow. It is not clear to me that this is especially unsafe given how prevalent it is.
E-1016 camloks using 4/0 90deg cable are rated for 400A (compliant with 400.5(A)(2)). If you use the 17-series you can go to a 690A rating with 500MCM(!!). What usually gets people is the other termination ratings.