I doubt that you can hook 2 wires to one terminal on a CB. I would install a jb outside the panel and splice them. You can if room permits splice the wires in the panel and have one wire on each terminal of the breaker.dahualin said:I am trying to use one 60A circuit breaker in MDP to feed two disconnect. Can I connect two wires to one circuit breaker terminal? If I can, what I shall pay attention to? Thanks.
Dennis Alwon said:I doubt that you can hook 2 wires to one terminal on a CB. I would install a jb outside the panel and splice them. You can if room permits splice the wires in the panel and have one wire on each terminal of the breaker.
weressl said:Since the terminals are designed to accomodate stranded wires that are nothing else but multiples of smaller wires, there is no reason why you would not be able to use multiple cables consisting of strands of the same size.
iwire said:No reason.....other then the NEC violation you would create.
iwire said:No reason.....other then the NEC violation you would create.
jrannis said:Which would be.......... drum roll.......
jrannis said:Which would be.......... drum roll.......
Southpaw said:Check with your electrical inspector to see if they permit splices in panelboards before you execute the work.
Technically this is not kosher as I am not aware of panelboards listed for splices.
Southpaw said:I personally don't see the problem with splicing in the panelboard but I have worked with several that had strong feelings that this was not permitted.
iwire said:110.3(B) and 110.14.
weressl said:It is NOT a violation of the code IF the CB meets these conditions.
Since the terminals are designed to accomodate stranded wires that are nothing else but multiples of smaller wires, there is no reason why you would not be able to use multiple cables consisting of strands of the same size.
iwire said:Of course, we even talked about that in this vey thread. :smile:
We also mentioned that it would be a very rare 60 amp circuit breaker that had single terminals rated for more then one 6 AWG.
It just a cover your rear code thing, I agree with your thought here..
It just comes down to being listed for that use. :smile:
weressl said:Just as an excercise, if you interested parttaking in it, walk up to a number of CB panels, both residential, industrial and commercial and report back to us how many small branch circuit panels you find where is NO doubled-up wires under at least one circuit breaker.
weressl said:Just as an excercise, if you interested parttaking in it, walk up to a number of CB panels, both residential, industrial and commercial and report back to us how many small branch circuit panels you find where is NO doubled-up wires under at least one circuit breaker.
iwire said:I don't have to, I have been seeing it for all my time in the trade. :smile:
It matters not.
The fact that it will work matters not.
The agreement with the states that I am licensed in requires I follow the NEC, even when I think I know better. :smile:
It does not have to make sense.......it just has to meet code....and be safe.
weressl said:...and I think it demonstrates that sometimes the Code has NOTHING to do with safety, just arbitrariness.
The problem with that is that the people who apply the Code in practice will not develop a valid sense of danger.
When they see that misapplication of the Code does not result in any danger, they will relax in rigorously following every word of the Code. That will result in being lax in areas where one can not.
That in turn will result even more restrictions being written into the Code such as the AFCI and wider and wider application of the GFCI's.
weressl said:...and I think it demonstrates that sometimes the Code has NOTHING to do with safety, just arbitrariness.