12- 107 - (645-5(e)): Reject
SUBMITTER: Rick Zupan, Lake Oswego, OR
RECOMMENDATION: Revise 645-5(e) read as follows::
(e) Securing in Place. Power cables, f l exible metal conduit,
liquidtight flexible metal or nonmetallic conduit, type MI cable, type
MC cable, type AC cable, communications cables, connecting cables,
interconnecting cables and associated boxes, connectors, plugs and
receptacles that are listed as part of or for, information technology
equipment shall not be required to be secured in place.
SUBSTANTIATION: There is an apparent conflict between this
section and Section 645-5(d)(2). This change and the accompanying
change to 645-5(d)(2) should resolve this.
PANEL ACTION: Reject.
PANEL STATEMENT: There is no conflict between the two sections.
645-5(e) pertains to listed equipment. 645-5(d)(2) is for field-wired
equipment.
NUMBER OF PANEL MEMBERS ELIGIBLE TO VOTE: 14
VOTE ON PANEL ACTION:
AFFIRMATIVE: 12
NOT RETURNED: 2 Kelly, Laney