Should also not need changed if set properly at initial install and nothing else has been changed.Changing the setting does not alter the circuit.
Should also not need changed if set properly at initial install and nothing else has been changed.Changing the setting does not alter the circuit.
Changing the setting does not alter the circuit.
Why are you limiting it just to altering the circuit, when the code clearly states, " when the branch circuits or overcurrent devices are altered, installed, modified, relocated, repaired, or replaced"?
Changing the starter probably isn't seen by most as altering the branch circuit.What part of changing out a starter is altering the branch circuit unless you actually do change the branch circuit?
Maybe the starter was damaged for some other reason, and you're simply changing the starter out to what was there before.
My comment on the "Altering" part wasn't directed at the branch circuit, it was in reference to "Altering" an overcurrent device,,, which an overload is in fact an "overload device".
I wouldn't think the rule would apply by simply adjusting an overload one way or the other.
Hence my suggestion that the rule applied to the wiring on the line side of the starter not on the load side of the overloads.
Hard for me to explain in writing... oh well.
JAP>
The bc starts before the contactor at the bc ocpd. I would say replacing or reworking anything downstream of the bc ocpd alters the bc.
I don't see that literally touching it has anything to do with "when the branch circuits or overcurrent devices are altered, installed, modified, relocated, repaired, or replaced".That may be, but, if so, this seems to be another one of those , you touch it, you're upgrading it rules.
JAP>
Sounds like the question is whether the starter is part of the branch circuit, i.e. where the outlet(s) are. Might depend on the wiring method from starter to motor, not sure. A cousin to the "is a switch an outlet?" question.
Cheers, Wayne
I don't see that literally touching it has anything to do with "when the branch circuits or overcurrent devices are altered, installed, modified, relocated, repaired, or replaced".
OTOH, it would be an adder the electrician could justify fairly easily by claiming the inspector might demand it. Most people are well aware that inspectors can be very arbitrary in their enforcement practices. An extra thousand bucks is not that big of a deal in the grand scheme of such things. Especially if the pool gets shut down for some period of time over it.
Art 100 definition of branch circuit I'd say includes motor controls, switches, receptacles, etc. that carry current of that circuit.Sounds like the question is whether the starter is part of the branch circuit, i.e. where the outlet(s) are. Might depend on the wiring method from starter to motor, not sure. A cousin to the "is a switch an outlet?" question.
Cheers, Wayne
Motor circuits get higher short circuit and ground fault protection in general as it is necessary to allow starting. The branch circuit conductors however are still protected from overloads by the motor overload protection whether it be integral to the SCGF device, the motor controller, a stand alone device, or even integral overload protection within the motor itself, which is somewhat common on single phase AC motors.I read somewhere that Motor Overload protection does not fall into the category of branch circuit protection.
JAP>
Motor running protection (i.e. overload relay) is not the same as motor over current protection. The NEC has different rules rules for both of these types of devices, so I would consider the starter and overload as not being part of the branch circuit.
Funny how if you remove them how they interrupt the circuit and the motor doesn't work thoughMotor running protection (i.e. overload relay) is not the same as motor over current protection. The NEC has different rules rules for both of these types of devices, so I would consider the starter and overload as not being part of the branch circuit.
Is a receptacle in the circuit count as part of the branch circuit?The NEC requires branch circuit wiring to be a minimum of 14A using #14AWG conductors. Motor starter and contactors do not have a minimum rating, the NEC simply requires them to be able to handle the motor current shown in the tables.