I hope someone will post the actual definition.
Since you asked (2017):

Branch Circuit. The circuit conductors between the final overcurrent device protecting the circuit and the outlet(s).

Outlet. A point on the wiring system at which current is taken to supply utilization equipment.

Premises Wiring (System). Interior and exterior wiring, including power, lighting, control, and signal circuit wiring together with all their associated hardware, fittings, and wiring devices, both permanently and temporarily installed. This includes (a) wiring from the service point or power source to the outlets or (b) wiring from and including the power source to the outlets where there is no service point. Such wiring does not include wiring internal to appliances, luminaires, motors, controllers, motor control centers, and similar equipment.

Cheers, Wayne
 

jap

Senior Member
Occupation
Electrician
Since you asked (2017):

Branch Circuit. The circuit conductors between the final overcurrent device protecting the circuit and the outlet(s).

Outlet. A point on the wiring system at which current is taken to supply utilization equipment.

Premises Wiring (System). Interior and exterior wiring, including power, lighting, control, and signal circuit wiring together with all their associated hardware, fittings, and wiring devices, both permanently and temporarily installed. This includes (a) wiring from the service point or power source to the outlets or (b) wiring from and including the power source to the outlets where there is no service point. Such wiring does not include wiring internal to appliances, luminaires, motors, controllers, motor control centers, and similar equipment.

Cheers, Wayne

This pretty much tells the story.
Thank You,
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
Yes, as long as a motor starter is "similar" to a "motor, controller or motor control center," then it's not part of the premises wiring system, so it can't be part of the branch circuit. Which would mean swapping it out does not involve modifying the branch circuit. Just don't cut or extend the line side or load side conductors connected to the motor starter. : - )

Cheers, Wayne
 

kwired

Electron manager
Location
NE Nebraska
Funnier that if you remove the motor it does not function either, but the motor is not part of the branch circuit. :)

Sent from my Pixel 4a using Tapatalk
Yep, or the splices in a box near middle of the run, or the local disconnect within sight of the motor....
 