680.22(A) Receptacles
That may be the best argument yet, 400.7(A)(6) or (8) specifically allows cord to be used but 400.7(B) requires those cords to be energized from a receptacle.
Yet, what if 400.7(A)(7) "Prevention of the transmission of noise and vibration" is also a condition???
Could we not call this a pendant and use 400.7(A)(1)? Such as
210.50 General.
Receptacle outlets shall be installed as
specified in 210.52 through 210.63.
(A) Cord Pendants.​
A cord connector that is supplied by a
permanently connected cord pendant shall be considered a
receptacle outlet.
Yeah I noticed that and wanted to use it to prove my point but I really figured that would be stretching it for the installation pictured. I can't honestly say I believe they used that cord to stop the transmission of noise when the pump itself looks hard mounted and hard piped.
Is it a 'pendent' when it comes out the side of a box on the floor?
I really do not think it is so I did not bring the pendent issue up.
In my mind a pendent hangs from above.
Main Entry: pen?dent
Variant(s): or pen?dant \ˈpen-dənt\
Function: adjective
Etymology: Middle English pendaunt
Date: 14th century
1 : jutting or leaning over : overhanging <a pendent cliff>
2 : supported from above : suspended <icicles pendent from the eaves>
3 : remaining undetermined : pending
So hardwiring the pump motor (or any motor for that matter) with a "rigid" conduit would be acceptable???
I'd say the wiring of the pump motor with cord was, in part, to mitigate vibration. What I was asking is if the inclusion of this reason alleviated the 400.7(B) requirement to plug into a receptacle.
Strangely yes.
But there are hard wiring methods that are flexible like LFMC.
To each their own, IMO the electrician did not use cord to stop vibration, they used cord because it is easy. :smile:
I don't know the answer to that question, the whole section seems to have evolved over many code sections, IMO both 400.7 and 400.8 could stand for 'do over'. :smile:
Where in 680 21 does it state that 400 type methods are acceptable for Pool Motor Branch circuit wiring?
It is moot since it does not specifically mention this as an option. For the pump side 3' or less and terminating in an attachment type grounding plug yes, the branch circuit side, no.
Tom:-?
Strangely yes.
I realize "rigid" methods are acceptable by code. Common practice says otherwise... :D
Perhaps... but that's not an available option for either uses permitted or not :grin:
Addendum: Regarding 400.8 Uses Not Permitted, a motor is not a structure per NEC, nor is a short transition from a fixed wiring method thereto a substitute for such... IMO.
I'd say!
Grammatically, the use of the word and, instead of or, in 400.7(B) means all three of the mentioned criteria, i.e. 400.7(A)(3, 6, and 8), must be a condition of usage in order for the receptacle requirement to be valid... ;):grin:
As far as I know motors are built or constructed, they do not grow from motor seeds. That makes them structures. :D
So you are saying structure, appliance, and utilization equipment are all interchangeable concepts under the NEC??? :grin: