Question:
How do I handle 690.14 (4) and 690.14 (5)
I would like to use a Switchboard to COMBINE twelve Utility Interactive Inverters.
I view this section as no more than six switches for DISTRIBUTION without a main disconnect
I could virtually parallel all twelve inverters together in a Polaris Lug after the disconnect at each inverter and before the main Disconnect. NOTE: there are no branch circuits connected to this system and 690.64 (B) should not apply.
Does the six disconnect in 690.14 (4) apply if there is no ?load? such as branch circuits involved.
I will only be COMBINING the AC inverters together to a much larger conductor.
How do I handle 690.14 (4) and 690.14 (5)