695 requires that the OC devices within the fire pump controller be rated to carry the locked rotor current of the fire pump motor. I have a 250 hp fire pump motor that is connected ahead of the Main service in its own section, there are no other OC devices ahead of the fire pump controller. The locked rotor current of a 250 hp is something like 1825 amps.
The fire pump controller has a data plate that rates the controller at 250 hp. The controller also has a transfer switch. Both the normal power and emergency power OC devices are rated at 400 amp.
Is this correct? The controller is UL listed and rated at 250 hp, but the 400 amp breakers do not appear to be rated high enough for the 1825 amp locked rotor current.
I do not believe they E power breaker is required to be rated for Locked rotor current.
I believe the normal power does?
The fire pump controller has a data plate that rates the controller at 250 hp. The controller also has a transfer switch. Both the normal power and emergency power OC devices are rated at 400 amp.
Is this correct? The controller is UL listed and rated at 250 hp, but the 400 amp breakers do not appear to be rated high enough for the 1825 amp locked rotor current.
I do not believe they E power breaker is required to be rated for Locked rotor current.
I believe the normal power does?