But fine they are not.That's not it...
According to the op:
That does not sound fine to me.I am having issues with gfci breakers tripping when installed on 7.5 hp single phase pump motors
Again from the OP:
Same comment.how do you fix this issue?
But fine they are not.That's not it...
That does not sound fine to me.I am having issues with gfci breakers tripping when installed on 7.5 hp single phase pump motors
Same comment.how do you fix this issue?
But fine they are not.
According to the op:
That does not sound fine to me.
Again from the OP:
Same comment.
...
...
There have been reports of people getting around this by adding a shielded isolation transformer ahead of the pump and grounding the shield so that the CM noise doesn't make it back to the breaker. There have also been mentions of adding ferrite beads to the wires going to the pumps as a way to suppress it too, I have never heard back if that worked or not.
...
Post #23 tells you exactly why.thank you all for your input
...
...
so again, I am asking why does the GFCI breaker trip?
folks please understand that we are not dealing with a 3 hp intelliflo or similar type pump. there is no vfd or vsd involved here. it is truly a single phase motor.
someone mentioned previously that they heard of Pentair pumps tripping gfci breakers! this is NOT the same application.
The capacitors...........tell a different story.Post #23 tells you exactly why.
No. A GFCI is a specifically listed Class A device under UL943.Would these be acceptable? View attachment 19746Selectable trip from 5 to 30 ma
Thanks.No. A GFCI is a specifically listed Class A device under UL943.
presuming both have same instantaneous trip point.
GFCI in the places where NEC is used is a device that responds to leakage current outside the intended circuit conductors, listing requirements for such devices want them to trip if leakage is more then 4-6 mA. They do not respond to short circuits or overloads, though there are types that are incorporated into circuit breakers - but the GFCI function is still a separate portion of those units and when they trip on short circuits or overloads that is the thermal-magnetic components that is tripping.
OP needs to somehow determine if his GFCI breaker is tripping on GFCI functions or thermal-magnetic functions.
OP needs to somehow determine if his GFCI breaker is tripping on GFCI functions or thermal-magnetic functions.
Post #23 tells you exactly why.
GFCI to NEC is the class A 6mA protection intended for personnel protection. Levels higher then 6mA are GFP, intended for equipment protection.@Jraef
I was looking at some other GFCI devices and they do offer a Class C device with higher mA ratings. however im not sure if this would be appropriate. the NEC doesn't specify, only stating it as GFCI protection for personnel. Littlefuse and NSS both offer these and it could be an option?