@jamesco
thanks for your questions jamesco
just to clarify, these are 3 isolated incidents at different locations all together.
Yes, I understood from your posts, 3 different locations.
the distance from breaker to motor is less than 20'
That rules out my thinking maybe it was an induction or capacitance issue during initial high inrush current on the branch circuit wiring, causing an imbalance on the 2 ungrounded conductors which might be causing the sensing coil in in the GFCI to trip open. 20' is nothing
the wire size is #8 or #6 THHN, I don't recall. the motor FLA is 30.4 so 125% still falls under 40 amps.
Even using NEC 430 to size the branch circuit wire #8 is all that is needed. 20' is short.
I don't recall if the main panel is 3 wire or 4 wire but it is 120/240 volt
voltage leakage through the motor windings was a thought but all three motors? its possible! we were thinking of wiring up a brand new motor to test this as we have one on hand.
Common denominator? Same motor manufacture. By chance have you tried to contact the manufacture directly about your problem? Speak to an EE?
- Three different pump locations.
- Branch circuit wiring length is approx 20'.
- All 3 GFCI breakers are CH.
- The breaker is slightly sized less that 200% of the motor FLA name plate rating. Motors start up fine, every time, when using a standard 2P 60A CH breaker.
- The motors are installed at 3 different locations.
Can it be the CH GFCI breaker that is at fault? Possible.
But I believe you stated in your thread the manufacture is/has had complaints of their motors causing GFCI breakers to trip open on start up.
Is it the insulation resistance of the start winding breaking down/leaking voltage, ever so small to cause at least a 5ma or 6ma current to flow to case/frame of the motor, during the high inrush current through the start winding when the motor is trying to start?
IF not could it be the start capacitor MFD selected by the manufacture that is causing a leading/lagging PF on the branch circuit causing the sensing loop in the GFCI to trip the breaker open?
This may sound dumb. If the conduit for the motor branch circuit wiring is big enough pull the wires out, (at just one of the 3 pump locations) and twist the 2 hots together keeping the twisted maintained from the breaker to the motor controller. As for the EGC wire do not twist it with the 2 hots. Just pull it back in straight along side the 2 twisted hots.
.