jaggedben
Senior Member
- Location
- Northern California
- Occupation
- Solar and Energy Storage Installer
That's a fair point. Another fair point is that the rule is overly conservative and the loophole doesn't result in an unsafe installation. The output from the solar/battery would have to exceed 200A for the busbar to exceed 200A, even if the sum of the load breakers were also 200A (in compliance with the rule).What is the difference, electrically speaking, between a 90A breaker in a panel and 90A of OCP on the other end of a conductor set connected to feedthrough lugs on that same panel? There is none that I can see; the NEC's silence on this point is, as you say, a loophole.