Elect117
Senior Member
- Location
- California
- Occupation
- Engineer E.E. P.E.
Your line to neutral and line to ground voltage measurements mean more than the line to line. They can tell us if you are experiencing a issue that should be addressed rather than a tap change.
I would also add, that if the transformer is undersized or the conductors are at a minimum that can also cause a voltage issue.
More importantly, make sure they aren't trying to use 230V motors on a 208V. That is a common issue.
And the utility is probably within limits. Most have rules that are about 10% of the designated voltage. Most supply closer to 5%.
5% of 480 is 456V. So anything more than 456V and they might not consider a tap change on the utility side. It could be a shared bank or shared transformer with other customers and if those customers are closer to the source transformer, they would have a higher voltage.
Having lower voltage is typically better than running on the higher side.
I would also add, that if the transformer is undersized or the conductors are at a minimum that can also cause a voltage issue.
More importantly, make sure they aren't trying to use 230V motors on a 208V. That is a common issue.
And the utility is probably within limits. Most have rules that are about 10% of the designated voltage. Most supply closer to 5%.
5% of 480 is 456V. So anything more than 456V and they might not consider a tap change on the utility side. It could be a shared bank or shared transformer with other customers and if those customers are closer to the source transformer, they would have a higher voltage.
Having lower voltage is typically better than running on the higher side.