Elect117
Senior Member
- Location
- California
- Occupation
- Engineer E.E. P.E.
I got a call because the walk-in cooler condensing motor had been replaced by the HVAC guy, two of the new motors burned that had been replaced.
Motor will run at minimum 200v
While taking voltage reading they been reading 193volts between phase.
Sent from my iPhone using Tapatalk
I know you will be able to solve their issue with all of the advice already given, but I would add to the list verifying the the HVAC guy's motor voltage minimum, conductor sizing, and maximum current rating.
200V rated motors should be okay within a range. Or at least that has always been my understanding. If the voltage is on the lower side of the rating, then the current increases to compensate. The cheapest solution is still to get the service voltage increased, or change the dry type transformer taps, but I would, if you had the time, verify the conductor and motor ratings.
My concern is that you will get the voltage fixed, but the motors might still fail if the issue is the combination of the conductor sizing and voltage. I wonder if he replaced the motors twice, checked voltage and it was within range those times, but this time needed to find something to blame. And since it is summer, and very hot (at least here), the voltage is lower. Those other times, it could have been winter and the voltage was fine. Or there is dust accumulation, the walk in door isn't sealing properly causing the motor to run for extended periods, etc. Upping the wire size can help with the effects of overloading. If the conductor is already oversized to the MOCP then that is definitely not it.