Roger, I agree with your method. I used that in a duplex on Tuesday, it worked out better than I could have hoped.
m73214 said:According to my calcs, you would need 3/0 CU to supply a 120V,20A load with a max voltage drop of 3.6V @1000'.
1793 said:With this answer I come up with 1/0 for EGC.
iwire said:In fact using 8/2 NM on a 20 amp circuit will create a 250.122(B) violation.
Dnkldorf said:Bob, how?
The egc is already upsized?
iwire said:It is but not enough to comply with the requirements of 250.122(B)
Table 250.122 shows that 15, 20 and 30 amp circuits require an EGC that is sized to a 1:1 ratio with the circuit conductors.
250.122(B) requires the ratio to be maintained.....no matter how strange and costly the results are.
Dnkldorf said:I don't see this.
Tbl 250.122 is showing me that a 20a circuit requires a #12 min EGC. It says nothing about a ratio.
Where did you see this ratio being required?
(B) Increased in Size Where ungrounded conductors are increased in size, equipment grounding conductors, where installed, shall be increased in size proportionately according to circular mil area of the ungrounded conductors.
250.122 Size of Equipment Grounding Conductors.
(A) General. Copper, aluminum, or copper-clad aluminum equipment grounding conductors of the wire type shall not be smaller than shown in Table 250.122 but shall not be required to be larger than the circuit conductors supplying the equipment. Where a raceway or a cable armor or sheath is used as the equipment grounding conductor, as provided in 250.118 and 250.134(A), it shall comply with 250.4(A)(5) or (B)(4).
(B) Increased in Size. Where ungrounded conductors are increased in size, equipment grounding conductors, where installed, shall be increased in size proportionately according to circular mil area of the ungrounded conductors.
Equipment grounding conductors on the load side of the service disconnecting means and overcurrent devices are sized based on the size of the feeder or branch circuit overcurrent devices ahead of them. If the ungrounded conductors are increased in size to compensate for voltage drop, the equipment grounding conductors must also be increased proportionately.
Example
A 240-volt, single-phase, 250-ampere load is supplied from a 300-ampere breaker located in a panelboard 500 ft away. The conductors are 250 kcmil copper, installed in rigid nonmetallic conduit, with a 4 AWG copper equipment grounding conductor. If the conductors are increased to 350 kcmil, to what size must the equipment grounding conductor be increased?
Solution
Step 1.
Calculate the size ratio of the new conductors to the existing conductors:
Step 2.
Calculate the cross-sectional area of the new equipment grounding conductor. According to Chapter 9, Table 8, 4 AWG, the size of the existing grounding conductor has a cross-sectional area of 41,740 circular mils.
Step 3.
Determine the size of the new equipment grounding conductor. Again, referring to Chapter 9, Table 8, we find that 58,436 circular mils is larger than 3 AWG. The next larger size is 66,360 circular mils, which converts to a 2 AWG copper equipment grounding conductor.
Dnkldorf said:Hypotheticaly here.
A piece of 8-2NM 20' long feeding a piece of equipment, on a 20a breaker, is a violation of 250.122b?
The EGC in this case would satisfy 250.4(a)(5) wouldn't it?
iwire said:Nothing hypothetical here...it would be a direct violation of 250.122(B)
Strange but true.
iwire said:Good morning gentlemen and thank you both.
I did some searching and found the handbook commentary.
1793 said:I thought this what I did in my post. Just looking at the numbers. If we took the #8 up to 3/0, that 916%. then the #10, 10380, would increase by 916% to 105,460.8, to 1/0 @ 105,600?
Dnkldorf said:How can a #10 EGC provide a low enough impeadance to clear a 40A fault, and not be sufficient enough to clear a 20A fault?