infinity said:If you look at 250.122 you'll see that a 20 amp OCPD requires the same size EGC as current carrying conductors. Therefore the ratio required ratio is 1 to 1.
So by that you could not use a 8/2 w#10EGC romex for a 20 amp circuit due to the undersized EGC in the cable?