80 circuit panel?

Status
Not open for further replies.

kbsparky

Senior Member
Location
Delmarva, USA
It is my understanding that the 42 circuit limitation for most panelboards and load centers will become a thing of the past once the 2008 edition of the NEC is adopted. The argument was that rule was implemented 80 some years ago when the use of rubber-covered conductors was prevalent, and installing more than 42 circuits in a single panel could overheat to the point of starting a fire.

Conductor insulation, wiring methods and overcurrent equipment have improved significantly in the time since then, so it would be logical that such an outdated requirement would be rescinded.

It has been pointed out in another thread here that some manufacturers make panels for use in other countries that do not have this limitation. Case in point from a recent listing for a 200 Amp panel on eBay from Canada:

5c64_1.JPG


Here we can plainly see that this 40 space panel is capable of handling up to 80 circuits.

Since the trend is to standardize the Codes from the US and Canada (meaning uL and CSA among others), this would seem to be what is in store for us?
 

bphgravity

Senior Member
Location
Florida
Here is a post I made regarding the topic on another Forum:

The 42-space rule is truly an obsolete code that really doesn't need to exist any longer. The original rule was established in 1933 after several fires (the most famous being the 1928 fire at the Waldorf Astoria in NYC).

At the time, Rubber insulated conductors were the norm and would easily overheats when one too many were installed in panelboard enclosures. At the time, UL did not provide the current requirements for "space" which is now provide in excess when in compliance with UL 67. With the use of 90?C insulated conductors and loading limited to 75?C in most cases, this problem doesn't exist anymore.

Also, Canada does not have this restriction and there does not appear to be any reported problems with panelboards containing more than 42 overcurrent devices.
 

cowboyjwc

Moderator
Staff member
Location
Simi Valley, CA
Remember that the 42 circuit limit is only for "Lighting and Appliance Branch-Circuit Panelboards". One having more than 10% of its overcurrent devices protecting lighting and appliance breanch circuits.
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
this panel is probably almost exactly like what you can buy here in the US. you'd only get 80 circuits using tandem breakers. if you buy a 6 space panel, it says its capapble of 12 circuits, and so on.
 

LAYMAN JOE

Senior Member
Its a 40 space panel.Add breakers rated for two connections would make it an 80 circuit panel. 80 circuits but still less than 42 breakers.
 

iwire

Moderator
Staff member
Location
Massachusetts
I am not following you Joe.

Right now we are limited to 42 overcurrent devices.

One 'twin breaker' is two overcurrent devices
 

yanici

Senior Member
Location
Atlantis
Occupation
Old Retired Master/Journeyman Electrician
I for one am waiting in gleeful anticipation for these 40/80 circuit panels. When the tandem afci's are introduced, we'll all be able to cook our hot dogs, for the game, on them. Just think of them as a kitchen small appliance.:grin: :grin:
 

LAYMAN JOE

Senior Member
iwire said:
I am not following you Joe.

Right now we are limited to 42 overcurrent devices.

One 'twin breaker' is two overcurrent devices

The manufacturer of that panel left "40 spaces". Yet the sticker states "80 circuits". I dont think they meant the panel is rated for 80 overcurrent devices (that would be a violation of NEC). I think square D (in this case) considers two wires terminating onto one single pole breaker as two circuits. Two circuits taking up one space. That way they can say our panel can have 80 circuits when we know that it would only be 40 circuits. (ooh, Ill get the one that can have more circuits). I think its simply a marketing ploy... Sorry for the confusion.

0f57_1_sbl.JPG
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Joe,
That panel is for Canada and they do not have the 40 overcurrent protective device limit like the NEC now has.
Don
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
LAYMAN JOE said:
The manufacturer of that panel left "40 spaces". Yet the sticker states "80 circuits". I dont think they meant the panel is rated for 80 overcurrent devices (that would be a violation of NEC). I think square D (in this case) considers two wires terminating onto one single pole breaker as two circuits. Two circuits taking up one space. That way they can say our panel can have 80 circuits when we know that it would only be 40 circuits. (ooh, Ill get the one that can have more circuits). I think its simply a marketing ploy... Sorry for the confusion.

0f57_1_sbl.JPG


incorrect. two wires on one breaker is still one circuit. a tandem breaker is two ocpd's. 40 tandems = 80 circuits. 40 sp's = 40 circuits, no matter how many wires.
 

LAYMAN JOE

Senior Member
brantmacga said:
incorrect. two wires on one breaker is still one circuit. a tandem breaker is two ocpd's. 40 tandems = 80 circuits. 40 sp's = 40 circuits, no matter how many wires.


I agree! Please dont misunderstand me. 40 tandem breakers is 80 circuits. 40 sp breakers with two wires on it is still only 40 circuits, not 80.

I thought I was clear in stating my opinion that its a play on words by square D (a marketing ploy). They give you 40 spaces, say it can have 80 circuits, and sell it in the US where it would be a violation to have more than 42 circuits.
Why would they advertise a product that would violate NEC? It doesn't make sense. It must be a marketing ploy for the do it yourself home owner. As I said:
That way they can say our panel can have 80 circuits when we know that it would only be 40 circuits.


Im not the best at clearly communicating through writing, sorry.
 

iwire

Moderator
Staff member
Location
Massachusetts
Joe the 42 limit is being removed and never existed in Canada.

Under the 2008 NEC we will be able to install 40 tandems in a 40 space panel that will result in 80 overcurrent devices or 80 circuits in one panel
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
iwire said:
Joe the 42 limit is being removed and never existed in Canada.

Under the 2008 NEC we will be able to install 40 tandems in a 40 space panel that will result in 80 overcurrent devices or 80 circuits in one panel


Does everyone agree that this is a good idea?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
infinity said:
Does everyone agree that this is a good idea?

I do--- 80 tandem arch faults- someone else said they wouldn't have to heat their basement. I might try grilling hot ogs on it.
 