Look familuar Mr.Kwired
It does to me, that is a primitive one line drawing I made of a service that I worked on.
It was a Main lug only switch gear rated 1,600 amps.
Look familuar Mr.Kwired
My reference was the six feeder overcurrent protective device. I see that as part of the question. The feeders make up the load for the service.
Im so sorry I got my wires crossed. No disrespect
Can't say I am familiar with Eaton's products, but that mains cabinet is likley available in 200, 400 and 600 amp versions as well. So whoever installed this must have had a load calculation of 600 or more or figured that if the last meter were ever used it could go over 600.
If you bring feeders into this it just confuses the issue, we are talking about service conductors and the rules are different.
Please tell us what section that exception is part of and which code year. I looked a little in 2014 where I thought it may be from yet don't find it so far. Knowing what section this a part of helps answer your question as it only is exception to the main text it is following. There may be more then one section with similar exception sometimes though.I was ignorant of this exception. Just curious, would this exception apply to the split bus panels ?
"Exception No.3: Two to six circuit breakers or sets of fuses shall be permitted as the overcurrent device to provide the overload protection. The sum of the ratings of the circuit breakers or fuses shall be permitted to exceed the ampacity of the service conductors, provided the calculated load does not exceed the ampacity of the service conductors."
230.90(A)