I believe that this condition needs to remain. It is a natural fact of life if you have equipment attached to building steel, and also have an equipment grounding conductor. Since the steel is likely to remain and the EGC is required, you are stuck with multiple paths in your 'bonded metal'.
You could _minimize_ this current flow if you replace your separate conduit feeder system with one large conduit or two conduits each with a three phase set of conductors. By placing your conductors closer to each other you minimize the magnetic field that they project into the surrounding space.
However I don't see this parasitic transformer with shorted secondary as a significant problem. It will increase voltage drop in the feeder slightly, and it may slightly reduce fault current in the event of a short circuit, but beyond this I don't see any sort of safety issue.
powerelectronic said:
Jon, would you please explain to me how you would go about confirming the ground? as I am in the state of confusion.
Drive has its own ground bus, there is no one common ground bus inside the electrical panel.
I was asking about the supply transformer. Have you confirmed that the supply transformer is actually electrically connected to the building grounding electrode system?
If the drive has its own ground bus, what is it bonded to? Is there electrical continuity between the drive ground and the panel?
-Jon