PT said:As per your diagram, the center of your wye is connected to ground, it is not also connected to to the load? You have a capacitor bank, that can also be factor in your mystery current.
Some drives are very sensitive, sometimes we install AVR or TVSS to protect them from over-voltage.
finally we open up the transformer, see how it is connected internally.
here it goes:
-ground conductor fed from Motor center, to capacitor bank, to transformer primary(delta)side.
-ground conductor then goes through lug (that is clamped down on bottom of transformer frame), then go as continuous loop through the wye center (X0 of secondary side)
-then continue going to the electrical panel with 6 insulated conductors (L1,2,3, shown in picture at the beginning of the posting).
-overall there is NO NEUTRAL wire in the electrical panel. there are single phase motors connected across L1,2, or l2,3, or l1,3.
would drives be affected if capactor bank is on the primary side of transformer, and drives are part of derived system?
I have to admit that I am puzzled... where about that most likely find the line to ground fault? what cause the overvoltage (paths).