I am doing a 277/480 service where the utility will be installing a 500KVA transformer. They gave me a fault current of 37K. After calculating the reduction from the service entrance conductors, I still was a little over my breaker ratings, so I asked for a photo of the name plate to run the calculation using actual transformer impedance (5.2%) to see if that would give me a better deal, and using that figure with 80% power factor in the MH calculator, I got 14.5K. Does that seem right? I just want to make sure I am not making a silly mistake somewhere - I wasnt expecting that much o a difference. Presumably the 37K figure is from a chart with the lowest possible impedance unit they could ever conceivably use?
The other question is, while double checking my formulas, I came across something in a cooper/bussman publication that I dont understand. They have a chart for "typical transformer impedance values" and it has two columns, one is "%Z" and the other is "suggested X/R ratio used for calculation." Could someone explain those two values?
Thanks!
The other question is, while double checking my formulas, I came across something in a cooper/bussman publication that I dont understand. They have a chart for "typical transformer impedance values" and it has two columns, one is "%Z" and the other is "suggested X/R ratio used for calculation." Could someone explain those two values?