37kA @ 12.47kV sounds high unless you're near large generation or a large substation.
I also have never used PF as part of my fault calcs. Impedance Z% is the total of R%+jX% not P and Q.
sounds high 550 mva of fault
pf can usually be ignored
only influences offset from symmetrical
pf = cos(arctan x/r)
and it is related to S = P + jQ
in phasors v/z = i
so Z determines the i ph shift which is related to the pf by
S = v (i*)
in other words the reactive load X (of Z) determines pf arctan(Q/P)
only comes into play with transient and subtransient
symmetrical isvthe same other than ph angle