Here is the text of the email I received from the POCO (engineer?) RE fault current:
Assuming that is what he meant to say, didnt cross columns, etc, They must be assuming 1.6%Z. That seems super low. Maybe they lump together pole mounts in that chart - dont they typically have a much lower Z than padmounts? The charts in here on page 6
http://www.cooperindustries.com/con...ch_Lib_Short_Circuit_Current_Calculations.pdf
Give an even higher value of 51500 for a 500 kva. Has anyone actually seen such low Z values?
The table I’m looking at shows a max short circuit current of 37,600 Amps at the transformer for a 3-phase 500kVA 480/277 V transformer.
Assuming that is what he meant to say, didnt cross columns, etc, They must be assuming 1.6%Z. That seems super low. Maybe they lump together pole mounts in that chart - dont they typically have a much lower Z than padmounts? The charts in here on page 6
http://www.cooperindustries.com/con...ch_Lib_Short_Circuit_Current_Calculations.pdf
Give an even higher value of 51500 for a 500 kva. Has anyone actually seen such low Z values?