A GFCI...an FPE panel...AL wire...and the unqualified.....Almost a fire!

Status
Not open for further replies.

frizbeedog

Senior Member
Location
Oregon
GFCI Meltdown!

DSC00628.jpg

DSC00634.jpg



It burned through the box! But I'm thinking the circuit breaker should have tripped before this.

DSC00627.jpg


Yes. That was AL wire you saw. What's that symbol on the right? :roll:

DSC00633.jpg


It's not that difficult a task, but unqualified is unqualified. A rental property and likely maintenance folks involed.

House wired with AL throughout, and an FPE panel.

Was called to replace this GFCI and Box, copper pigtails of course, and will replace the circuit breaker for the affected circuit with new or tested/refurbished.

Above and beyond that I would love to hear what other actions you would propose. I know what I would like to do. :wink:

From what I saw, the house was close to being burnned to the ground.
 
iwire said:
Nice photography. :cool:

What are you using?

Sony Cyber-shot, DSC-H3

8.1 mega pixels

10x optical zoom

ISO 3200

I don't know what all them numbers mean but it's a relatively inexpensive camera.
 
frizbeedog said:
Both?

The fact that the breaker did not trip is the bummer.
I'm not completely convinced, based on what I see in the pictures, that any breaker would have tripped. A 5 amp fault, or resistive connection at a similar magnitude, can burn down a house and never trip a breaker. Dare I say, that's what brought AFCI's about.
 
480sparky said:
Copper will do the same thing if it's not tightened properly, though.
Copper and alum have different expansion coeficients so when the circuit is cranked up like with a blowdryer the copper/brass only expands a little while the al expands a lot and it has no where to go so it squeezes out to the sides. Hair gets dry and device cools down the alum pushed out the sides and now the screw connection is loose. Hairdryer comes on again the next day now the whole thing gets even hotter a little bit more every day untilyou get a fire in the wall.
 
quogueelectric said:
Copper and alum have different expansion coeficients so when the circuit is cranked up like with a blowdryer the copper/brass only expands a little while the al expands a lot and it has no where to go so it squeezes out to the sides. Hair gets dry and device cools down the alum pushed out the sides and now the screw connection is loose. Hairdryer comes on again the next day now the whole thing gets even hotter a little bit more every day untilyou get a fire in the wall.

I understand all that. But who's to say the connection wasn't tight enough to begin with, copper or aluminim notwithstanding?
 
mdshunk said:
I'm not completely convinced, based on what I see in the pictures, that any breaker would have tripped. A 5 amp fault, or resistive connection at a similar magnitude, can burn down a house and never trip a breaker. Dare I say, that's what brought AFCI's about.
I fully agree but am not even sure that an AFCI would detect this problem. The high heat produced by a poor connection may not be an arcing fault and the AFCI would act just like a standard breaker in that case, with the exception that the heat could melt the insulation and cause a ground fault which the AFCI would react to.
 
don_resqcapt19 said:
I fully agree but am not even sure that an AFCI would detect this problem.

Given the damage to the device pictured, some arcing must have been happening at some point during it's meltdown.
 