a water source heat pump with MOCP of 15A - fused disconnect size

Status
Not open for further replies.
Location
VA
Occupation
electrical engineering
Greetings,

We have a water heat source pump with MOCP of 15A. Would it be acceptable to specify a 30A fused disconnect switch with a 15A fuse in it in the circuit powering up this pump? My biggest concern is someone potentially installing a 30A fuse in the 30A fused disconnect switch by mistake making the installation non-NEC compliant. Any thoughts?
 
As retired stated don't worry about future idiots. The NEC doesn't care about them so neither should you.
 
Greetings,

We have a water heat source pump with MOCP of 15A. Would it be acceptable to specify a 30A fused disconnect switch with a 15A fuse in it in the circuit powering up this pump? My biggest concern is someone potentially installing a 30A fuse in the 30A fused disconnect switch by mistake making the installation non-NEC compliant. Any thoughts?

You can use a non-fused disconnect if the heat pump doesn't state "Max Fuse Only" or something to that nature
 
Greetings,

We have a water heat source pump with MOCP of 15A. Would it be acceptable to specify a 30A fused disconnect switch with a 15A fuse in it in the circuit powering up this pump? My biggest concern is someone potentially installing a 30A fuse in the 30A fused disconnect switch by mistake making the installation non-NEC compliant. Any thoughts?
There is no way around that with fuses...fuses 30 amps or less have the same physical size so the a fused disconnect that you are going to be using a 15 amp fuse in will always have a 30 amp rating.
 