We frequently have the service point at the secondary spades so I will comment also:I am just curious if you can clarify in your state of Illinois this transformer you speak of that contains inside it a NEC service point,
- Is it under exclusive control of the utility?
- Is it on property owned or leased by the electric utility?
- Is is for the purpose of transformation or transmission?
- Is it located in legally established easements or rights or way?
1. I would say the transformer is under exclusive control of the utility, but it has customer owned conductors inside. If I need to service or inspect them I will call the utility for access.
2. Typically they are on private property. The utility gets an easement for their equipment.
3. Clearly it transforms the voltage. I would say it is not part of the transmission system.
4 see #2. Sometimes they can be on public property, which is often called the right of way.