Dear All,
Our specs restricted conduit bending as minimum two 90 degree bend or equivalent but don't say anything about offsets like below. Could you please tell me that there is a restriction at NEC for offsets?
Thank you very much. Is the same considering valid for the offset below?
That's a 3 point bend aka "saddle" We consider it a 90 degree bend. The only restriction of bends or offsets that I know of is 360 degrees between pull points.