I agree with Bob, the interior of the switchboxes looks like it would be accessible by unscrewing the coverplate and the switches.Switch box connections not accessible is more of a problem than the fact the cables are embedded - am I correct? Cables start at the top of the wall.
II. Installation320.10 Uses Permitted. Type AC cable shall be permittedas follows:
(1) For feeders and branch circuits in both exposed andconcealed installations
(2) In cable trays
(3) In dry locations
(4) Embedded in plaster finish on brick or other masonry,except in damp or wet locations
(5) To be run or fished in the air voids of masonry block ortile walls where such walls are not exposed or subjectto excessive moisture or dampness
The real question, to me, from only seeing this photo, is: Is the masonry wall below, or above, grade? If it is below grade, and the cable is, in fact, type AC, then it is exposed, I would argue, to a damp location and is prohibited from having been installed there.
Grade line is above the box - maybe a foot or so.
Grade line is above the box - maybe a foot or so.
I don't see how being below grade makes it damp. It appears to be a finished space to me which pretty much precludes it being "damp".
I don't see how being below grade makes it damp. It appears to be a finished space to me which pretty much precludes it being "damp".
It used to be easier to understand what the Article on Armored Cable (AC) was saying was a dry location with respect to uses permitted for AC.
I just checked my copies of the '81, '84 and '87 NEC and the "Uses Permitted" included the phrase "or are below grade line" as an area where only a special form of AC, type ACL (that has a continuous lead sheath, instead of paper) was allowed. Back then AC was in Article 333.
Location, Damp. Locations protected from weather and
not subject to saturation with water or other liquids but
subject to moderate degrees of moisture. Examples of such
locations include partially protected locations under canopies,
marquees, roofed open porches, and like locations,
and interior locations subject to moderate degrees of moisture,
such as some basements, some barns, and some coldstorage
warehouses.
Location, Wet. Installations underground or in concrete
slabs or masonry in direct contact with the earth; in locations
subject to saturation with water or other liquids, such
as vehicle washing areas; and in unprotected locations exposed
to weather.
I don't see an issue with the switch box. it looks like you can get at the connections just by removing the cover plate. the stub out is kind of peculiar though.
is that NM? If so it can't be embedded but if there is a void it can be fished down to the box.
I'd guess someone is gluing drywall on the block hence the 1/2" shims behind the plate.
If the wiring wasn't installed to the Code of its day, then, there is something else at play. "Today's Code" hasn't got anything to do with it, in my opinion.since that requirement appears to have been removed why would it matter any?
I am inclined to agree that the code at the time of the installation is what matters.If the wiring wasn't installed to the Code of its day, then, there is something else at play. "Today's Code" hasn't got anything to do with it, in my opinion.
There are areas of water seepage through the foundation, though not specifically in this area.
We're talking about AC. Not MC.I would certainly hope with all those new dimmers that require a full sized ground when ya'll keep sayin' AC you really mean MC...