I have read the threads about runing smaller wire than "normal" to AC units (inductive loads?) but never really grasped the concept.
208V 3 phase 17.5 ton AC
Specs say 90 amp MOCP.
# 4's or can I go smaller?
You certainly may, but it's overkill in most installations.I didnt think you sized the wire according to the MOCP. I definitely could be wrong.
Breaker 90a or less (but don't).90 amp MOCP.
Wire for 83a or more.MCA = 83 amps
You certainly may, but it's overkill in most installations.
Breaker 90a or less (but don't).Wire for 83a or more.
Well, yeah...but I have followed threads where they are talking about running #10 or 12 on a 50 amp breaker for ac condensers and wondered if the same twisted logic applied here.
I have read the threads about runing smaller wire than "normal" to AC units (inductive loads?) but never really grasped the concept.
?
It is rare to have the minimum circuit ampacity that close to the maximum overcurrent size for an AC unit, but as others have said the code permits you to install the wire to match the minimum circuit ampacity and connect that wire to the maximum permitted OCPD.MCA = 83 amps
thwn
#4 looks like to me.
what you will find is the ocpd is usually 125% of the mca
Well, yeah...but I have followed threads where they are talking about running #10 or 12 on a 50 amp breaker for ac condensers and wondered if the same twisted logic applied here.
LOL-- it is not twisted logic. What you are refering to is art. 240.4(G) which allows us to use #12 wire at 25 amps , #14 at 29=0 amps and #10 at 35 amps. Also the a/c units have a built in overload protection which protects the branch circuit from running at a higher ampacity than intended. The OCPD that we install only protects for short circuit and ground fault.