Sorry if this question has already been asked :
Im having trouble getting an absolute answer about name plate ratings on motors, particularly on AC Condensers for residential dwelling units. Copper prices are so high these days, i am trying to save some money by calculating the smallest branch-circuit feeder needed to feed my AC condensers for track homes.
For Example today i checked out a unit set yesterday and the name plate read:
1/6hp 220v 60hz
Minimum supply circuit ampacity : 25A
Minimum Fuse Size : 30A
Maximum Fuse Size : 40A
I would like to figure out how these numbers came to be?
I check out table 430.148 for 1/6 HP and saw that the Full-Load Current in Amperes is 2.2
430.22 led me to 125% for a single motor Full-Load Current.
2.2x1.25= 2.75 Amps.
Now Where do i go?
How do i get the name plate values the manufacturer listed?
If the Nameplate is correct, assuming the unit is rated @ 75C, are you saying i could use a 12-2 NMC per (310.16 & 240.4(d)) and install a 30,35, or 40 Amp breaker?
Im having trouble getting an absolute answer about name plate ratings on motors, particularly on AC Condensers for residential dwelling units. Copper prices are so high these days, i am trying to save some money by calculating the smallest branch-circuit feeder needed to feed my AC condensers for track homes.
For Example today i checked out a unit set yesterday and the name plate read:
1/6hp 220v 60hz
Minimum supply circuit ampacity : 25A
Minimum Fuse Size : 30A
Maximum Fuse Size : 40A
I would like to figure out how these numbers came to be?
I check out table 430.148 for 1/6 HP and saw that the Full-Load Current in Amperes is 2.2
430.22 led me to 125% for a single motor Full-Load Current.
2.2x1.25= 2.75 Amps.
Now Where do i go?
How do i get the name plate values the manufacturer listed?
If the Nameplate is correct, assuming the unit is rated @ 75C, are you saying i could use a 12-2 NMC per (310.16 & 240.4(d)) and install a 30,35, or 40 Amp breaker?