looking for area of code that would tell distance required from a air condensing unit disconnect to the exterior water faucet bib. any ideas anyone?
How would 110.26 apply?Originally posted by allenwayne:
Unless the ahj is being a pain 110.26 might be his out sucks huh
110.26(F)(2) Outdoor. Outdoor electrical equipment shall be installed in suitable enclosures and shall be protected from accidental contact by unauthorized personnel, or by vehicular traffic, or by accidental spillage or leakage from piping systems. The working clearance space shall include the zone described in 110.26(A). No architectural appurtenance or other equipment shall be located in this zone.