You can install a 20 amp breaker and it will be safe but may not work.
The rule is that the breaker must be capable of carrying the starting current of the motor or the equipment.
It's not really a minimum "size" rule, but a minimum performance rule.
I was getting carried away when I said you could install a 20 amp breaker. I would bet money that's not going to work.
How would they know the minimum size breaker that would work except for perfect conditions. Ambient temp, voltage drop and age of the unit. Under the right condition it might start with a 35 amp breaker and then not work on a really hot day.