Need to do an energy calc for the PC on a residence. They want both tons and KW. I have the tons (4) but that is all the AC guy gave up. I remember a basic translation existed but its been a long time. Voltage is 240 Nominal. I can guess and throw down 30Amps but that's not any fun. Any help?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
It can vary depending on the efficiency of the system components. I would just look up a few random 4 ton unit spec's and take it from there.
 

tw1156

Senior Member
Location
Texas
These are "loose" values that I have used in the past:

1kVA per ton can be a rough start and we'll use it for quick calcs when we have no additional information and are trying to anticipate service size to a building. I'm unsure if this is true for residential though.

~350 - 400sqft / ton on average, but this varies by space and location.
 

florida-sparkey

Senior Member
Location
Pinellas Park, Florida
Occupation
Master Electrician
I have also looked up a few and they seem to be around 17 RLA, FANS 1.2 FLA. This is close to what most have suggested so going to use 18.5A / 4.4KW and call it Friday!
Thanks!
 

Ingenieur

Senior Member
Location
Earth
Last edited:

florida-sparkey

Senior Member
Location
Pinellas Park, Florida
Occupation
Master Electrician

Thanks for the help. I really appreciate it.

I think you are looking at min circuit ampacity? Unless I am misreading it, the 4 ton unit on your sheet has 21.2 RLA and 1 FLA FAN. A little larger but I have found Trane to do that. If I hadn't already done the clac and sent it I would of used your load. Its the largest I have seen of the 5 I looked at. In any case, +-5A is not a big deal in this calc.
 

florida-sparkey

Senior Member
Location
Pinellas Park, Florida
Occupation
Master Electrician
that is a direct conversion without unit eff considered

in the US htg/clg calcs are done in btu's and that is how units are rated
12000 btu = 1 ton clg capacity

units are elec/mech overall eff ~50%
so you can use 1/2 of the calculator kw value
but obviously best to have specific unit data or at least similar units

Thanks, I was wondering how it got to 60A. Even half is higher than the units you posted links to. I think the "pull a few random data sheets" is the most realistic so far.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
that is a direct conversion without unit eff considered

in the US htg/clg calcs are done in btu's and that is how units are rated
12000 btu = 1 ton clg capacity


calc 4 ton ~ 14 kw or 58 a at 240/1
actual numbers 28-30 a or 7 kw

Are you assuming a COP of 2 or better?
 

Ingenieur

Senior Member
Location
Earth
Power equals volts times amps. Solve for amps. A = W / V = 14,000 / 240 = 58.33333 Amps.

cop = coef of performance
bssically output kw/input kw
it varies might be ss low as 1 if very hot outside > 100 f
and as high as 3-4 if inside temp ~ outside temp 70 F
the eff varies with the delta oat vs desired inside temp

so if the unit has a cop of 2
4 tons or 14 kw of clg can be done with 7 kw of elec
7000/240 = 29 a
 