Thanks kwired!
The 1K per ton is not even close to what some others or the calculator link were saying (they were at 30A up to 60A). That was my confusion and I was trying to understand how it could be so different. Ultimately, I used 4.4KVA and that seemed close to the spec sheets I read online.
I think 1.5 kVA per ton may be more realistic value, but 4.4 is pretty high. You sure the 30 to 60 amp you mentioned isn't somehow related to overcurrent protection device setting? 5 ton single phase unit - typically needs a 60 amp circuit breaker, but actual rated current draw of the compressor is more like 26-32 amps max.