accesible floor

Status
Not open for further replies.

garrisonm1

Member
Location
Maryland
working in a school and one of the classrooms has a 6 inch raise floor that is accessible. Is it legal to run mc underneath the floor to feed THE floorboxes and etc.
 
Re: accesible floor

I agree, unless the underfloor space is used for air supply. See 300.22(B). Then your MC cable may have to meet the requirements listed.

Steve
 
Re: accesible floor

Steve I think it would be all set under the provisions of 300.22(C)Other Space Used for Environmental Air.

No different than above a suspended ceiling. :)
 
Re: accesible floor

You are probably right, Bob, 300.22(C) would most likely apply. It has similar restrictions on MC cable, but not as many.

Since he did say it is in a classroom, the space probably isn't used for air handling.

Steve
 
Re: accesible floor

Originally posted by steve66:
You are probably right, Bob, 300.22(C) would most likely apply. It has similar restrictions on MC cable, but not as many.

Since he did say it is in a classroom, the space probably isn't used for air handling.

Steve
Unless the classroom in question is a computer or technology lab (most likely in a college setting) in which case it very well could be used for air handling. Though 6" seems a bit shallow for a computer floor.
 
Re: accesible floor

I think any MC cable is probably OK if the space is not used for air handling (i.e. it doesn't have vent panels in the floor and there isn't an air conditioner feeding the space under the floor.)

If the space is used for air handling, you will want to read the code sections mentioned.

Steve
 
Re: accesible floor

Steve, 300.22(C)(1) specifically allows any MC without an overall nonmetallic covering to be used in this Other Air Handling Space

Roger
 
Re: accesible floor

Roger,

Yes, but if it is an air handling space, I still think he should read (B) and (C) and decide which applies. If (B) applies, there is another requirement for the MC jacket.

I know its unlikely, but it is possible that the primary reason for the raised floor is as an air handling duct.

Steve
 