Well, this will depend on the amperage-the voltage is irrelevant. Big difference between a 15 or 20 amp recep. VS a 50 amp as to how to how to specify a box.
 
I thought I read 50 amp in the OP 😅😅

My answer is still the same on the box.

20a or small 30a would be single gang
Large 30a or 50 would be 2 gangables

Deep as possible in either case. What you lose on the perimeter can be made up in depth
 