See the second reposting, he is not talking about the load shed device in that post, DR is talking about using tandems to free up enough space for the EV breaker, which is fine, as long as the panel is listed for their use.Here’s my understanding of how it works based on reading data sheets in the link:
This device is wired from an regular breaker in the panel just like any other load. The EVSE is connected to it. This device simply shuts off the EVSE based on the load on the service.
I don’t think he mentioned tandem breakers, either!