kingpb said:Regardless of the NEC MINIMUM, or what the inspector wants. It can be flat out dangerous to have a resistance to ground at the rod greater then 25 Ohm.
References to follow should be IEEE 142 and IEEE 80.
I don't know if I'd call it hatred... more of a playful banter.barbeer said:I sense alot of negativity and inspector hatred here and am not sure why! We have a big red book that tells us almost exactly what to do. For the record....I have been a Journeyman electrician for ten years and an inspector for only a year.
Go easy guys.
jtester said:I believe it's unrealistic to apply IEEE 80 to commercial grounding.
In the 40+ years I've been in the electrical trade I've never seen a ground rod test to 25 ohms or less. Even if it did, I don't know how or why it would be safer than one that tested to 50 ohms.
Jim T
As long as there is a second ground rod, there is no code requirement to reach the magic 25 ohm barrier.The fact that you have not seen one test out to 25 or less, tells me there is a lot of out of compliance installations. That's a shame.
kingpb said:Regardless of the NEC MINIMUM, or what the inspector wants. It can be flat out dangerous to have a resistance to ground at the rod greater then 25 Ohm.
I haven't looked back to see what the scuffle was, I'll just say this: generally, with inspector rant threads around here, the anger revolves around two attributes of the inspector: unwillingness to read and/or enforce the code as written (which goes along with making up their own code), or a questionable interpretation.barbeer said:I sense alot of negativity and inspector hatred here and am not sure why! We have a big red book that tells us almost exactly what to do.
Your skin will get thicker with more experience as an inspector, I reckon.For the record....I have been a Journeyman electrician for ten years and an inspector for only a year.
Go easy guys.
I too would welcome an explanation. Although I am not familiar with those standards, word of their proven protection methods have not graced this forum in the two years I've been here, that I've noticed.kingpb said:Regardless of the NEC MINIMUM, or what the inspector wants. It can be flat out dangerous to have a resistance to ground at the rod greater then 25 Ohm.
References to follow should be IEEE 142 and IEEE 80.
infinity said:I've done it. What happens? Nothing. Connect the conductor going to the rod to a 20 amp breaker and read the current flow with an ammeter. If you had 12 ohms the meter will read 10 amps. 6 ohms reads 20 amps.
Bob NH said:If I clear the area around the ground rod and apply 120 volts through a 100 watt bulb, through an insulated wire connected to the ground rod, by pressing a momentary switch while I measure voltage relative to the grounded conductor and current through the insulated wire, it is not dangerous except to earthworms and grubs.
I think one big reason is a matter of source impedance of the meter itself. I could be wrong, but here's my theory.Bob Anchorite said:Since we are on the subject of the famous 25 ohm rule... the guys who sell the ground resistance meters say that your regular ohm meter will not read the ohms to ground accurately and that you need a real ground resistance meter. Is this true, if so please explain... at $1200 to $2500 for this type of meter I would like to see why etc...