Re: Additional Panel
Bennie the majority of us are subject to inspections under the requirements of the NEC, we do not do our work on a piece of paper where we can control all outside influences.
Adding switches and breakers on the feeder does not change anything.
Under the rules of the NEC the addition of switch changes a service conductor to a feeder.
OK, six loadcenters on a wall, all supplied by one set of service conductors.
Would the panels be service panels?
Yes they would all be service panels.
Now spread the panels throughout the building. The only thing that changes is the location. Are they still service panels?
No, they are not now service panels, as there would be a required OCPD and switch back at the service entrance.
As Don said, call the panels whatever you want but the important point as far as the NEC is concerned is the location of the
Service Disconnect
Line side of the
Service Disconnect is treated one way, the load side
Service Disconnect is treated another way.
Don't you ever get tired of this conversation? :roll: