Re: Additional Panel
Bennie,
If we don't take an EGC to the second panel and use the grounded conductor for that purpose, we will have a silghtly higher voltage between noncurrent carrying parts that are bonded to the second panel and things like water pipes or building steel that are bonded at the building disconnect. This voltage will be equal to the voltage drop on the grounded conductor between the second panel and the first panel. If the EGC from the second panel would be connected to a common metallic system that also has a connection to the first panel, we have created a parallel path for grounded conductor current.
Don
Bennie,
If we don't take an EGC to the second panel and use the grounded conductor for that purpose, we will have a silghtly higher voltage between noncurrent carrying parts that are bonded to the second panel and things like water pipes or building steel that are bonded at the building disconnect. This voltage will be equal to the voltage drop on the grounded conductor between the second panel and the first panel. If the EGC from the second panel would be connected to a common metallic system that also has a connection to the first panel, we have created a parallel path for grounded conductor current.