Re: Additional Panel
Most 100 amp panels are only rated 100 amps non-continuous and for that 3 AWG is correct.
Highkvoltage, you do not have to feed a 100 amp panel with 1 AWG to use it at 100 amps, 3 AWG is fine.Originally posted by highkvoltage:
Your conductors would have to rated for 125%. To feed a 100 amp subpanel and for you to have the ability to have 100 amps at the subpanel your branch circuit would have to be #1 THHN (Table 310.16).
Most 100 amp panels are only rated 100 amps non-continuous and for that 3 AWG is correct.